sparky71

Sat my 2391 in aug got the results back over the phone failed
Did not say what area I failed on
Is there any way to revise and remember all gn3
 
Hi sparky71 sorry to hear this.......I can help you if you want to pm me some stuff you think you may of struggled on and maybe give you some guidance on stuff that will Probably pop up......I didn't even look at GN3 and I passed it and know I would pass it every single time.

First of all can you remember whereabouts you struggled?
 
Right ok well on mine I had a earth fault loop diagram.......that you can get say 11-12 points just for drawing it

Then I had a IR test

Bullet point the whole procedure.

Warning signs
Warn people of test carrying out
Isolate and lock
Sensitive equipment removed & linked out

Etc etc

Then at the end check results against bs7671 to make sure comply then reinstate circuit to original condition ......there's 2 extra points at the end

Then I had a test sheet there was like 7 zs results that were below the maxium stated but not within 80% of so they were flagged, then there will always be a IR of like 0.23 n-e with say 299 either side of it, just watch out for them.

The earth electrode test popped up on mine that's a GN3 thing as hard to explains on here you would need the illustrations.......15 marks again rekon I proble got about 7 on that as I don't know that fully which I regretted when I left the exam!
 
I would say Somthing like this......

Put up warning signs and warn people I testing

Dead test so safe isolation and lock off

Check machine complies with gs38 ....2-4mm tip, finger guards, inline fuses, 1000v insulated leads, no defects on machine, calibration certificate.

Then set machine on the low ohms scale

Null your test leads out or take reading of leads and subtract from result. (would just stick with null)

Prepare conductor for test.

Take end to end reading of line, & nuetral they should be withing 0.05 Then the cpc reading should be 1.67 times greater.

Then cross over the outgoing Nuetral to the incoming line and vice versa. And take the results at each point o the circuit to ensure no loops etc again they shoul be withing 0.05

Then do the same with your line & earth and test at each point the highest reading should be the one recorded, if a result is particularly higher then this will be a spare wired that result shoul be recorded.

Reinstate circuit to original condition and proceed to next test.


Should get close to maxium marks for that
 
No worries.....all broken down its not bad at all just all in one go seems a bit daunting, just go for a little bit of a time at revision. One test procedure each night and you will blast it!

Then section A just little stuff to boost your marks I.e Minor Electrical Installation works certificate instead of minor works

don't forget the 3 seperate documents after a installation is Electrical Installation Certificate, Schedule of Inspections, Schedule of test results

Check sharp edge on Conduit, inspection lids secure, conduit screwed up correctly,......that's another 3pointer
 
Your maxium zs for each different type and size of breaker are on what used to be page 49 of red regs but will have to check what page green.....think like page 53

You can calculate your zs by taking your R1 + R2 value of a circuit and adding that To your Ze (reading from consumer back to sub)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2391
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
sparky71,
Last reply from
p11jor,
Replies
21
Views
1,902

Advert

Back
Top