R

robbo_blah

Hi,

I am due to sit my 2392/1 practicals soon and during the course of my revision have come up with some un-answerable questions.

2392:
1. Are we required to perform live Zs checks in addition to working out Zs for each circuit?

2391:
1. what percentage Inspections should be performed on the exam (I know its 10% in real life unless a discrepancy is found?)
2. what is the correct procedure for testing the 3 phase elements (this was not covered in any detail on my course)
3. is the phase rotation test required to be done?

Also if anyone can provide me with the makeup of the individual boards within each exam, I would be most grateful!

Cheers
 
Thanks to everyone for their experiences and advice. I managed to pass my practical 2391 today and passed my practical 2392 two days ago. I have already passed the 2392 theory so I only have to complete the 2391 written to complete my qualifications
 
Upvote 0
1 d

2 b

3 d

4 a

5 b

6 b

7 c

8 b

9 a

10 c

11 b

12 b

13 a

14 b

15 a

16 a

17 a

18 b

19 a

20 b

21 d

22 c

23 d

24 c

25 d

26 b

27 a

28 a

29 b

30 d
 
Upvote 0
agree with 2 didnt see for new circuit
18 is seperation between selv an lv so 500v 1.0M pg 41 gn3 tests between selv and other circuits
26 is asking for external earth fault loop max ze and as 0.35 is the only one there thats the one i chose

wait re read question 26 lol now i agree with iq its 26b
but its worded badly as usual was thinking tn-c-s but its refering to a tn-s system
so i only disagree with iq on 18
 
Last edited:
Upvote 0
26 is 1.85X.8 = 1.48

1.48-1.03 only leaves 0.45 left for Ze in order for the circuit to comply.

You might be getting confused with the ESQCR max Ze values for different earthing systems.
 
Upvote 0
yes mate i was lol
but i still think 18 is refering to testing for seperation of selv and lv mi insulation resitance 1.0M as the selv is employed in a area where lv is so 500v and 1.0M as you have to check between lv live conductors connected together and selv lives connected together
 
Upvote 0
so i only disagree with iq on 18

And quite rightly, I rushed in and didn't read the full question!

For any of my students reading this, I messed up question 26 just to show how important it is to read the question fully! :confused:
 
Upvote 0
iq why pir on 2 so to do a additinal new circuit you have to give a PIR as well as a EIC i thought you just had to confirm the existing was acceptable and would not be affected i am ow leaning towards 2C
relevent comments on existing installation which would be on the EIC lol

why do C&G word things so badly and confusing

I too rushed 2 , 18, and 26 are very sneaky lol just shows read a few times eh mate to be sure you understand the q
 
Last edited:
Upvote 0

Reply to 2392/1 practical exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
431
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top