Hey folks

sitting 2394 written exam tomorrow and have a few questions in my notes I need the textbook answers for.

1. State four practical steps that the inspector can take during the inspection and test process to ensure the safety of the users of the building, other than safe isolation.

2. State what would be verified when confirming that additional protection has been provided using RCD's

any references would be helpful

cheers guys
 
Place barriers
Place obstacles
Erect warning notices
Give audible warnings to the users of the premise

Cables are installed at a depth of less than 50mm and are not mechanically protected
RCD is <30ma for additional protection
 
1. rusty nails has given the stock answer., and gets all 4 marks.:coolgleamA:

2. That the Earth Fault loop impedance for the circuit/s is compliant, The RCD is 30mA, and trips within 40 mS at 150mA (5 times I delta N)on both half cycles. The mechanical test button functions properly.

GN3 will elaborate where i haven't.

Cheers................Howard
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2394 exam questions help
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Hogshaw,
Last reply from
barneybhoy,
Replies
6
Views
2,058

Advert

Back
Top