Possibly it might be worth checking on your level of current training, you say you are studying for the 2396 and so have presumably got a good existing background in electrical compliance.
You started the thread with a fairly high level design query but are now getting confused about basics.
Now I do not profess to know lots about the subject but I tend to work from first principles and apply common sense, this is not always a good idea for the wiring regulations!
Always remember that I am posting my ideas in a similar manner to the way you are posting yours. Always check back with your notes and ensure I am not making errors.
If you have reference books that state that the fault current should be determined at the extremity of the circuit then they are more likely to be correct than I am. However do check the reasoning and intent behind the reason why they are determining the fault current.
In your last post you ask if you should use one of two equations but the equations are the same equation just mathematically rearranged.
S= √ (I² × t) ∕ k
multiply both sides by k
S * k = √ (I²t)
square both sides (or multiply by √I²t which you know equals Sk)
S²k² = I²t
(and if you divide both sides by I² you get t=k²S²/I²)
either way works.
My reasoning for using the PFC as fault current when determining energy withstand or cpc suitability, as opposed to ADS disconnection time, is hopefully explained by the attached diagram.
You started the thread with a fairly high level design query but are now getting confused about basics.
Now I do not profess to know lots about the subject but I tend to work from first principles and apply common sense, this is not always a good idea for the wiring regulations!
Always remember that I am posting my ideas in a similar manner to the way you are posting yours. Always check back with your notes and ensure I am not making errors.
If you have reference books that state that the fault current should be determined at the extremity of the circuit then they are more likely to be correct than I am. However do check the reasoning and intent behind the reason why they are determining the fault current.
In your last post you ask if you should use one of two equations but the equations are the same equation just mathematically rearranged.
S= √ (I² × t) ∕ k
multiply both sides by k
S * k = √ (I²t)
square both sides (or multiply by √I²t which you know equals Sk)
S²k² = I²t
(and if you divide both sides by I² you get t=k²S²/I²)
either way works.
My reasoning for using the PFC as fault current when determining energy withstand or cpc suitability, as opposed to ADS disconnection time, is hopefully explained by the attached diagram.