Seen an ammended control panel today sporting a bs 60898 DP type C 2 amp mcb controlling 24v dc.
Usually weidmuller etc din rail fuseblocks and links.
Something I am missing?
Boydy
[ElectriciansForums.net] 24 volt dc
No, still can't see it.
Boydy
I can't see what your problem is or what your missing?? lol!! MCB's protecting DC circuits is perfectly acceptable, when they are designated suitable for DC protection by the manufacturer!!
BTW, the Schneider web page you linked too, is from they're USA site...
An understanding of the functioning of mcb's perhaps?
C60HB, C60HC and C60HD are suitable for 24v DC .....
The number of poles required on your DC breaker is determined by the type of DC system you have:-
1- one polarity of dc supply is earthed
2- center point of the dc supply is earthed
3- insulated systems
As already mentioned you linked to a mcb designed to comply to UL requirements as areas including USA have differing regulations from us and the mcb's we use would not comply in their control systems..hence you have a differing dc rating and you have got yourself confused.
Hi,
Schneider MCB's are acceptable for DC provided you follow their guidance, they generally have to be down rated though. In their catalogue they have a page on 'DC operation of Miniature Circuit Breakers'.