Also i have looked at the relays and i have continuity across the relay that switches pin1 on the first PCB and on the other PCB i have continuity across the relay that switches pin 2.
Checking the relays R1 for pin 1 is std 5A capacity relay, R2 for Pin2 - they have used the high capacity version of the same relay type (10A) and R3 for Pin3 is a std 5A one again, all NO . So two poorly relays as well as burnt tracks,,,
 
Relays welded shut are consistent with the evidence so far. As I mentioned in #5, if two relays close at once (or one closes while another is welded) part of the main winding is shorted and the circulating current can exceed the supply current by transformer action. The impedance of the non-shorted section might be high enough not to blow the fuse at first, giving things a chance to overheat.
 
I've seen in at least one commercial design, and I'd do it that way myself, using changeover relays so that relay 1 applies power to one connection, only when relay 1 is off does it's NC contact pass power to relay 2, and similarly for power to relay 3. That way, barring an internal failure in a relay, it's impossible to cause the sort of "shorted section" fault described.
BTW, when running on fast (or to a lesser extent on medium) the the slow connection is typically at a significantly higher voltage than the mains supply - with the motor windings acting as an auto-transformer. I vaguely recall measuring over 400V to neutral on a a cooker hood fan motor.
 

Reply to 240V SP Ind Fan Motor wiring help in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The motor is a common AC 120v 60hz motor. I've seen a hundred of them around for various things. It is attached to a single vent squirrel cage...
Replies
2
Views
231
The white is the neutral. The black is hot to the light, brown is hot to the fan… (or other way round) I did this myself once, but it was in...
Replies
2
Views
503

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top