OP
weep
lol, yeah yeah, been wiring boilers like this for years
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 24v at switched side of room stat (230v) possible backfeed ? in the Central Heating Systems area at ElectriciansForums.net
i know what your saying but in all honesty, nearly every spark i know wires them this way and very very rarely do we get any issues. still doesnt solve the problem at hand, will check boiler terminals with switched live on Lr disconnected (safely of course ) tommorow.
Think Marvo hit the nail on the head in post two
The point is to ensure that if the boiler is switched off or a fault takes the internal fuse out then the whole system goes off. As you have wired it at the moment the Lr would remain live and so be feeding a live into the boiler despite the fuse having blown.
It's perfectly logical and sensible if you take a second to think about it, and I'm sure they have a good reason for doing it.
If lots of people do something wrong then it must automatically become correct?
Of course not and i aint getting into any arguments about it.
Everybody I know wires them according to the boiler manufacturers instructions, there are a few manufacturers who specify that they be wired this way.
The point is to ensure that if the boiler is switched off or a fault takes the internal fuse out then the whole system goes off. As you have wired it at the moment the Lr would remain live and so be feeding a live into the boiler despite the fuse having blown.
It's perfectly logical and sensible if you take a second to think about it, and I'm sure they have a good reason for doing it.
Most of the time theres a reason why a manufacturer specifies something, even if we cant see it. Ive done it myself, thought 'what a load of rubbish' then when ive had it explained thought 'ahhh i see!'
Above is a perfect example.
Just because 'it works' or 'ive been doing it for x years' doesnt mean were doing it right does it?
Its a bit like the 'ive been driving 50 years and never had an accident' syndrome
As far as im concerned, every days a school day ;-D
If lots of people do something wrong then it must automatically become correct?
Everybody I know wires them according to the boiler manufacturers instructions, there are a few manufacturers who specify that they be wired this way.
The point is to ensure that if the boiler is switched off or a fault takes the internal fuse out then the whole system goes off. As you have wired it at the moment the Lr would remain live and so be feeding a live into the boiler despite the fuse having blown.
It's perfectly logical and sensible if you take a second to think about it, and I'm sure they have a good reason for doing it.