25A MCB on 2.5mm kitchen radial | Page 2 | on ElectriciansForums

Discuss 25A MCB on 2.5mm kitchen radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

BS 7671 radials for 13amp sockets are 20amp wired in 2.5mm2 or 32amp wired in 4mm2 why are you considering using a 25amp cb?
 
All this iffing and whatifing, if the circuit is for a specific piece of equipment, the design it properly taking into account all the variables. If the radial is for socket outlets then use a 32 amp RFC, 20amp radial or 32amp radial
 
Well credit to the OP he has admitted there mistake, now looking at ways of getting it correct with minimal inconvenience.

I am sure we would all usually install a 32 amp circuit for a kitchen, unless we knew other wise what was going to be used in it.

A 25amp MCB may just be the answer they need to sort out the problem.
 
BS 7671 radials for 13amp sockets are 20amp wired in 2.5mm2 or 32amp wired in 4mm2 why are you considering using a 25amp cb?

I'm afraid i may be over 20A maybe 22-23A. I understand its not the best way around it, but I was checking if it is possible. For the cable to withstand the loading
 
I would seriously recommend the Guy stick in 2 20 amp circuits and forget all about it, well after testing certification and Part Peeing of course.
 
check out the time/current curves of 20A MCB. at 25 A should give her time enough to burn the dinner.
 
Well credit to the OP he has admitted there mistake, now looking at ways of getting it correct with minimal inconvenience.

I am sure we would all usually install a 32 amp circuit for a kitchen, unless we knew other wise what was going to be used in it.


A 25amp MCB may just be the answer they need to sort out the problem.


Thanks for the help, I have never thought of even putting in a ring and never have done in a domestic situation, just how I have always been told. So a 25amp MCB will be SAFE for the cable?
 
Thanks for the help, I have never thought of even putting in a ring
Not trying to be difficult or sarcastic Joey but that suprises me, I have never heard anyone not be trained in installing a ring main in a domestic setting. To be honest it is standard and school boy stuff. Out of interest Pal who trained you? a company or an individual?
 

Reply to 25A MCB on 2.5mm kitchen radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Norcal - thanks, belatedly. 'Tis the season when I don't get anything done, even though this project is near the top of the list. Per your...
Replies
7
Views
605
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top