Hi all,
Just planning a sub main to an outbuilding .
It will be 80 metre run, buried direct on a 63amp fuse .
So I am thinking of running 25mm swa but just been doing my calcs on whether I can use armour as Cpc. The outbuilding is going to be TT so no need of a bonding conductor on the submain.
After doing calcs in 2 core swa I get
99/51 x16 = 31.02
What I cannot find is csa of 25mm armoured to see if it is big enough .
If anyone could give me the answer it would be most appreciated
Reply to 25mm swa armour for cpc in the UK Electrical Forum area at ElectriciansForums.net
You would treat it as a TT installation.
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
I think the original was 'no lyrics'
5K
I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
nicebutdim