28A in 4mm cable 6.5kw hob | on ElectriciansForums
Discuss 28A in 4mm cable 6.5kw hob in the UK Electrical Forum area at ElectriciansForums.net
Portsmouth
i need to wire in an induction hob which is 6.5kw and the cable already chased in is 4mm and would be a real pain to replace for a bigger. I just wanted to know if it would be alright or play it safe with a 6mm?
Well Ref B gives you 28A max on 4mm t&e and the appliance is unlikely to draw all its 6500W at the same time, so 4mm should be fine unless a more onerous installation method has been used.
Ok, clipped direct gives you even more headroom.
Reply to 28A in 4mm cable 6.5kw hob in the UK Electrical Forum area at ElectriciansForums.net
I actually did it with a 4 core 4.0mm swa last week!
I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...