bartkusal

-
Arms
Joined
Nov 1, 2011
Messages
224
Reaction score
36
Location
London
Hello everyone, sorry but this one will be a long one. I am fairly new here, I used this amazing forum nearly everyday for 3 years now, but that will be my first post, this forum with its geniusmembers helped me through my courses, which I past with distinctions all theway. I done C&G 2330, C&G2382, C&G2391, C&G2399 and Part P course.So thank you all for your contribution..
I am hunting for some jobs to use it as my assessment for theregistration with those Part P bodies. Basically I was asked to price the job. The house is big four storey split in two, therewas a fire, I had to look for extent of damage and price up for rectification.Checked the premises, the only damage is 2 consumer units burned out, my mainconcern is cables, they all burned out and would be too short, so I will needto somehow extend them (maybe by crimping), or should I better replace thecables from CU to the first points (the later will change the price considerablyas there is a lot of cct). And do you think it could be more damage to thecables which I cannot see?
So I would like your comments on anypart of this thread, thanks in advance for your great contributions
Below is a copy of my letter witch Iintend to send to the client, there is more info on the installation, so feelfree to comment on anything you like, I am ready for some toasting guys, becauseI think the only way to learn is the hard one….


Dear client,
After what I seentoday at the premises, my main concern is the lack of consideration on thedesign stage of the installation, I am very surprised that this was not pickedup when you had the installation done 3 years ago as when I was told it tookplace.
Basically you have a property split in two:
1. Basement and Ground floors
2. First and Second floors
Both of them havetheir own supply meter and own 60 A distributors cut out fuses. Each of themfeeding (as much as I could see from burn out equipment) 15 way 100 A splitload consumer units??? This is absolutely not acceptable. Don’t want to be tootechnical, so what I am saying is that your load demand doesn’t match thesupply characteristics from your electricity supplier.
So taking that in consideration you must contact yourelectricity supplier and ask to upgrade your main cut out fuses to at least 80A or in fact 100 A each , stating thatelectrician strongly advised you to do that.
And we on other hand can do your side of installation.Having checked the extent of fire we can confirm that due to that you don’tneed a full rewire. We will need:
· Tracing and identifying what each circuit isfeeding (which can take fair amount of our time considering the size of theinstallation and all the labelling and identifications burnt out)
· To replace two consumer units with all mainswitches, RCD’s and MCB’s ,
· Extend or maybe replace up to the firstpoint the burnt out cables,
· Replace the damaged fluorescent light fitting inthe main entrance and maybe some smoke detectors.

Taking into account that you have an installation as new as3 years old and presumably no faults which we might need to rectify as we go,with all installation certificates supplied to us on our request, the price wecan estimate is( ),alllabour and materials included. Materials will be well trusted MK make. Anyextra works which might come up after we inspect and test your installationwill bring extra charges, but let’s hope that it will be straight forward andeverything will be covered by the price above.

So looking forward to hearing from you

Regards:

 
Re: 2x Concumer unit change

So it was an electrical fire then ?
If they cant give you any answers as to the cause of the fire or if they are even insured in the first place then i'd be very suspicious of getting involved.
To provide an accurate assessment of the situation you need ALL the information from the customer.
 
Re: 2x Concumer unit change

i think you right biff55, they where a bit too secretive about the whole thing from begining, I could smell something stincking here, I probably fallow your advice and find some stright forward job ( not that easy obviously) for my assesment...thanks again....
 
Re: 2x Concumer unit change

i think you right biff55, they where a bit too secretive about the whole thing from begining, I could smell something stincking here, I probably fallow your advice and find some stright forward job ( not that easy obviously) for my assesment...thanks again....

No worries pal , it sounds to me that they know damn well what caused the fire , they may even be partly responsible
for it , and they may not have proper insurance cover anyway.
Walk away , the whole thing sounds like bad news.
 
Re: 2x Concumer unit change

if your instinct tells you there's something fishy, walk away , or you could end up well out of pocket. i would explain that before you can quote the job, you need to do a thorough inspection and test first. this is chargeable and to be paid on completion of testing. (you don't get surgeons cutting someone open before a full and accurate diagnosis has been completed.) then, as long as you have been paid for the diagnosis, you can go ahead and prpare a quote.
 
Re: 2x Concumer unit change

Love you simpliness, this is something I strugling to learn, but I know that this skill have to be with me if I am about to work on my own and comunicate directly with clients. thanks much appreciated


You can have that one for free.

For the future, follow the same format.

State what you found, in simple terms and few words so a non technical customer can understand.
State what you propose to do.
List individual items, don't ramble on.
 
Re: 2x Concumer unit change

Way too many words for a fairly simple situation.


Dear Client,

After a cursery inspection we have found;

2 Consumer units fire damaged.
Cables connected to the C.U are damaged.
Fluorescent light in main entrance damaged.
Possible damage to smoke detectors

To bring the installation back up to standard will require;

1: New consumer units, including all MCB and RCDs. Also calculations to assess whether the incoming supplies are suitable.

2: Individual Circuits from each of these will need to be traced tested and assessed to determine how far back to replace the damaged cables. Initial view is fairly local to the Consumer unit.

3: Replace damaged fluorescent fitting and lamp, and diffuser (if originally fitted)

4: Verify smoke detectors work, replace where required.

Extra as yet unidentified work that may be required will be notified to you for your approval.


Full test certs etc supplied on completion.
Nice work snowhead. The only thing i would say is, somewhere in the letter you would need an estimate of costs.
 

Reply to 2x Consumer unit change in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
779
  • Question
IMO Better to do something about those ignoring regulations first! Current system is like having a speed limit but not enforcing anyone without a...
2
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top