testing an installation(that we have just finished) where the client want to choose a few circuits and check it against the test sheets, Now the circuits are 3- 240mm single core cables in parrallel (24 in total in a data centre) I have tested r1+r2 with 3 different fluke multi function testers that have been callibrated and i get different readings every time,as in 1 tester will give me 2 or 3 different readings on the same circuit , the next 2 or 3 completely different readings and so on,changed batteries, swaped leads, but nothing seems constant, doing my head in,one told me a 6m run had more resistance(0.05 no way) than a 70m run(0.01), only thing i can think of is Edmunsons can't callibrate properly and are ripping us of, think readings should all be about 0.00 -0.01 but getting -0.03 to 0.18( different every time)
 
You're trying to measure quite low values at the limit of the range/resolution of the instruments so any errors from probe contact etc. will appear to be amplified.

+/- 0.2 ohms I wouldn't really lose any sleep over.
 
Thanks for that, Fluke does seem a bit random compared to the meggers we used to use, is there a meter that can measure resistance in micro ohms?
 
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.
 
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.

You also need to know how to use a Ductor tester too, ...ie, test kit settings and testing position of current and potential spikes.... You'll also have to substantially bridge the cables at one end under test, as you don't use wander leads with this kit!! lol!!
 
ive tested for over 6 years with various meters and never come across a high Ze on a TNC-S. Now i've got this fluke 1652C ive found two seperate installations with the tnc-s Ze over 0.68!!!. is it the meter or just a coincidence???
 

Reply to 3 Fluke testers, different results? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
257
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top