testing an installation(that we have just finished) where the client want to choose a few circuits and check it against the test sheets, Now the circuits are 3- 240mm single core cables in parrallel (24 in total in a data centre) I have tested r1+r2 with 3 different fluke multi function testers that have been callibrated and i get different readings every time,as in 1 tester will give me 2 or 3 different readings on the same circuit , the next 2 or 3 completely different readings and so on,changed batteries, swaped leads, but nothing seems constant, doing my head in,one told me a 6m run had more resistance(0.05 no way) than a 70m run(0.01), only thing i can think of is Edmunsons can't callibrate properly and are ripping us of, think readings should all be about 0.00 -0.01 but getting -0.03 to 0.18( different every time)