Should the 3 Meter electrical reg. be reconsidered.?? Surely its "un-electrical" to deem mechanical protection as a suitable substitute for proper electrical protection?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 Meter rule? in the UK Electrical Forum area at ElectriciansForums.net
As above, do you mean the DNO 3m rule, or the stuff in reg 433.2.2 that let's you put the protective device in the run of the conductor in some circumstances, one of them being it's with 3m of the change of cross sectional area (and other additional requirements apply)?Should the 3 Meter electrical reg. be reconsidered.??
I see the two more as separate methods which can both be used for safety of Livestock and personnel. I don't think there is any suggestion one could/should substitute the other.deem mechanical protection as a suitable substitute for proper electrical protection?
Yes. And the reg in 434.3.(iv).Just a, personal view but I find it telling that the run of cable from the DNO, s cutout to the consumers main OC device is the only run of cable in a domestic installation whose length is not determined by the usual factors (volt drop, Fault loop Imp. etc). Its length is determined by the perceived risk of damage to the cable and the perceived consequences of unconventional fault protection (as I understand it). The 3 Meter length (some DNO, s stipulate 2 meters) is arbitrary not relying on a lot of science.As above, do you mean the DNO 3m rule,
Sort of.I must be getting my wires crossed on this
I'm assuming in relation to busbar it says you can tap off using smaller CSA cables up to 3M long
What does it say in relation to domestic tails ?