so I got a Nest installer from their site.
now are getting some where.When the heating engineer came to install the 3 nests (to control separate zones on the ufh and the water) we ran into issues.
The Nest heating engineer wired up the nests to control the ufh heating zones and that all appears to work as expected (nest 1 opens 4 actuators, nest 2 opens the next 2 etc). His issue arose when trying to switch on the boiler from the ufh wiring centre. I shall double check with him today that he's all good for the weekend and that he's confident everything will be wired correctly (and work as expected).All you need is a nest thermostat and a heat link for each zone. The Heat link will control the valve for each zone which in turns switches the boiler. Or in your case the heatlink controls the actuator or thermostat terminals on the UFH wiring centre which in turn switches the valve which switches the boiler.
As far as I can tell there are 2 x 3 core and earth (1mm) running from the wiring centre in the loft to the wiring centre by the ufh heating manifold. I assumed (incorrectly?) that this was to be used for control rather than control and power to the manifold/pump downstairs?
The one saving grace is that if it is wrong it's still possible to get a cable from the loft to the utility room if required.
The Nest heating engineer wired up the nests to control the ufh heating zones and that all appears to work as expected (nest 1 opens 4 actuators, nest 2 opens the next 2 etc). His issue arose when trying to switch on the boiler from the ufh wiring centre. I shall double check with him today that he's all good for the weekend and that he's confident everything will be wired correctly (and work as expected).