3 or 4 Pole main incomer? | on ElectriciansForums

Discuss 3 or 4 Pole main incomer? in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 8, 2017
Messages
12
Reaction score
2
Location
Newcastle
When ordering a 3 phase + Neutral DB, I forgot to specify that I wanted a 4 pole switch for the main incomer. What came was a 3 pole main switch with neutral link.

My question is why would you opt to use a 3 pole and neutral link instead of a 4 pole switch? Surely a 4 pole switch is always safer as completely isolating equipment from all live conductors (I.e any feedback etc) to work on?

I am newly qualified, I can’t see anything specific about this in the 18th edition so am keen on the reasons why you would choose one over the other.

Cheers
 
Back in the day when I used to be on the tools the sub boards were Merlin boards which were 3phase,
They all had 3pole switches with a neutral link, but Im sure in the main switch panel, the main switch would be a 4pole ACB,
This would have been a Tesco store done in the late 90s
 
With a TN system there is no need to disconnect the neutral to achieve a safe isolation because the neutral is reliably connected to earth. By having the neutral switched at the main switch you introduce the possibility that the neutral contacts could fail and cause all sorts of problems so it is generally thought to be better to avoid adding an unnecessary potential point of failure.
Where there is a need for the neutral to be switched to avoid danger then it is of course necessary to provide this facility and it becomes a bit if a lesser of two evils situation.
 

Reply to 3 or 4 Pole main incomer? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
574
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.
Replies
13
Views
1K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
726

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top