Hi
we have a 3 phase 63A isolator.
i have been asked to supply from this 3 x single phase 63A sockets. I have said this cannot be done because the neutral is only sized for the 63A supply. But now i am questioning myself. Help please
 
Because the neutral would still be the same size, yet potentially could be carrying 63 amps from each phase!!!!

- - - Updated - - -

The answer is yes you can do it, but ensure each single phase socket is fused individually.
 
sorry must disagree, as the op states he wants 3 x 63A Single phase supplies. Fully loaded you can have a current of 180 Amps flowing down the neutral. 3 phase machines are different, because any unbalanced currents just flow down the neutral.
 
sorry must disagree, as the op states he wants 3 x 63A Single phase supplies. Fully loaded you can have a current of 180 Amps flowing down the neutral. 3 phase machines are different, because any unbalanced currents just flow down the neutral.


What!!!!!!

Do you over sizer all your neutrals on sub mains to compensate for that?
 
sorry must disagree, as the op states he wants 3 x 63A Single phase supplies. Fully loaded you can have a current of 180 Amps flowing down the neutral. 3 phase machines are different, because any unbalanced currents just flow down the neutral.
What if you had a 3 phase 63 amp Distribution board with every circuit in it single phase and it was full to capacity?

- - - Updated - - -

What!!!!!!

Do you over sizer all your neutrals on sub mains to compensate for that?
Yeah why not :sifone:
 
sorry must disagree, as the op states he wants 3 x 63A Single phase supplies. Fully loaded you can have a current of 180 Amps flowing down the neutral. 3 phase machines are different, because any unbalanced currents just flow down the neutral.

Yes that is the worst case scenario, if only two phases were fully loaded simultaneously, and it is actually 1.73 X, every other combination would cancel out to a degree.
 

Reply to 3 phase 63A in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
632
  • Question
Three phase or single phase it is not correct.
Replies
1
Views
571

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top