Hi
we have a 3 phase 63A isolator.
i have been asked to supply from this 3 x single phase 63A sockets. I have said this cannot be done because the neutral is only sized for the 63A supply. But now i am questioning myself. Help please
 
OK. assume all 3 phases pull the same. neutral current =0.

take a possible scenario. L1 =63A, L2 = 10A, L3 =10A, N current will be around 53A. and you'll get similar results for any combinations. N current will never exceed 63A.
 
The end result is the neutral conductor should be designed to carry the most onerous current that could flow in it. Hence, under a pure resistive load condition, the neutral conductor needs to be the same size as the line conductor.
 
The end result is the neutral conductor should be designed to carry the most onerous current that could flow in it. Hence, under a pure resistive load condition, the neutral conductor needs to be the same size as the line conductor.
Well yes, but not 3 times larger which is where the thread seemed to be going at one time, to answer the OP=no problem providing the load for each phase does not exceed the protective device for that phase.

- - - Updated - - -

Yes hooray for Tel, but me and Diilb did try to tell everyone LOL
 
this thread =



[ElectriciansForums.net] 3 phase 63A

.............
 

Reply to 3 phase 63A in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
634
  • Question
Three phase or single phase it is not correct.
Replies
1
Views
571

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top