3 phase 70 KVA generator | Page 2 | on ElectriciansForums

Discuss 3 phase 70 KVA generator in the Commercial Electrical Advice area at ElectriciansForums.net

Ive just been reading this guide, and it suggests that the suppliers earthing facility cannot be relied upon for ADS, when the genny is in operation.
Now in my mind, this means that your earthing for the genny is required to be at TN levels (very very low on large gen sets), or MCB's with residual earth fault protection are required. Can anyone add to this please, and point me to documentation?

Thanks

John


You don't necessarily need TN values (always better of course) on generators, the main consideration is that you ALWAYS provide a 4 Pole changeover switch on 3 phase systems and never a 3 pole with solidly linked neutrals. A good 10 ohm TT earthing system should generally suffice for a generator installation...

Most generators of any size will (or should) come with it's own pretty comprehensive protection facilities, including earth fault protection, either via a multi function protection relay unit or incorporated within the units MCCB/ACB.
 
When I asked this question I overlooked a fundamental issue: the fact that your not relying on the rod for ADS, but to tie the genny down to earth potential.
The genny will already have a very low earth fault loop impedance because it will usually have a dedicated earth cable. I overlooked this too.
I was feeling ill though! Lol
 

Reply to 3 phase 70 KVA generator in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
410
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
743
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Even if it’s says that the neutral is bonded to the generator, you still are required to install a ground wire from the generator to the transfer...
Replies
1
Views
138
Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top