3 phase boiler install on domestic property

Hi all,

A customer is looking into the option of upgrading to a 3 phase power supply in order to get a new electric boiler system installed. They currently have a single-phase supply. They have an out-building with an electric car charger. Would an option be to have say a 1 way 3 phase board next to the main cut-out fuses and then have one of the phases supplying the out-building, one supplying the main consumer's unit and the 3rd phase supplying the boiler? Or would the main CU need to be split amongst the phases? I think from memory its at least a 10 way board. The main draw in the house is an electric shower. Thanks for taking the time to read.
 
i would be inclined to get customer to buy a 3 phase boiler. last one i did would have been 63A on single phase, but was only 21A on 3 phase. that meant the cable feed to the boiler was 2.5mm as opposed to 10.0mm. then in your case, i'd maybe have 1 phase for the house and outbiulding and 1 phase for the charger.
 
They have been advised by the boiler people that it will need to be 3 phase.

"boiler people" with common sense. that's got to be a first. can't be BG then? ??
 
i would be inclined to get customer to buy a 3 phase boiler. last one i did would have been 63A on single phase, but was only 21A on 3 phase. that meant the cable feed to the boiler was 2.5mm as opposed to 10.0mm. then in your case, i'd maybe have 1 phase for the house and outbiulding and 1 phase for the charger
Thanks, my concern was the balancing of the loads, as the car charger will only be on every now and again, in the evening.
 
I'm not sure about the UK regs but where I am the main DB or CU must have a single point of isolation for the entire electrical installation including all final circuits and sub-DB's etc. Hence the main CU would need to be 3-phase if the incoming supply is 3-phase.

I'd get the exact make and model number of the boiler and download the spec sheet. Often 3-phase boilers can be wired as single phase using the internal wiring option links. The current for the boiler configured as single phase might be too high however.
 
I'm not sure about the UK regs but where I am the main DB or CU must have a single point of isolation for the entire electrical installation including all final circuits and sub-DB's etc. Hence the main CU would need to be 3-phase if the incoming supply is 3-phase.

I'd get the exact make and model number of the boiler and download the spec sheet. Often 3-phase boilers can be wired as single phase using the internal wiring option links. The current for the boiler configured as single phase might be too high however.
Yes same here, needs to have a single point of isolation. I'm guessing that to run most efficiently that 3 phase would be best?
 
If they are going down the route of an electric boiler I would look into considering air source heating, in recent yrs it has developed enough to become more viable in the UK, I know 2 houses running it and it was -2 c outside and it had no problem heating the house and water up without tapping into its booster elements, given that your already planning on heating by electric it would be crazy not to use a system that can do the same job at a fraction of the billing costs.
 
If they are going down the route of an electric boiler I would look into considering air source heating, in recent yrs it has developed enough to become more viable in the UK, I know 2 houses running it and it was -2 c outside and it had no problem heating the house and water up without tapping into its booster elements, given that your already planning on heating by electric it would be crazy not to use a system that can do the same job at a fraction of the billing costs.
Yes, certainly worth considering. I don't really know much about them, can the existing heating system be incorporated into it or is it a case of ripping it out and starting again?
 
You would have to consult a supplier on that but as I understand it can be used on most household plumbing installs, radiators, underfloor piping etc, I cannot see why it cannot be adapted to an existing system, the two I was involved with were fully new installs including pipework but were new builds, I believe the crucial factor to viability of such systems is the energy efficiency of the building so it may not be suitable for older buildings, that you would have to discuss with the company who would supply the system.
 
You would have to consult a supplier on that but as I understand it can be used on most household plumbing installs, radiators, underfloor piping etc, I cannot see why it cannot be adapted to an existing system, the two I was involved with were fully new installs including pipework but were new builds, I believe the crucial factor to viability of such systems is the energy efficiency of the building so it may not be suitable for older buildings, that you would have to discuss with the company who would supply the system.
ok thanks.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Edders,
Last reply from
telectrix,
Replies
19
Views
5,290

Advert

Back
Top