Hi all,

Tested a building today and came across this, never seen it before.
3 phase circuit but was connected in the board over 4L3, 5L1 and 5L2. There havnt used 5TP as the circuit that any normal person would with ways available too. Ive coded this code 3 due to incorrect phase tape used. Is that all i can fail it on :(

Any help or feedback would be great

Thanks.
 
This is common enough across industrial installations with maintenance fitters who don't have a clue what they are doing. Come across this quite a bit. IMO C3 is fine at this point provided this is the only issue with the circuit. That's what I would record it as. Is this observation the only problem you have come across on this installation? What does it supply?
 
Thanks for the quick response mate. The installation is in a ok condition. The DB have recently been upgraded so would say the guy installing the DB was at fault :( Have a few other minor faults on the DB missing the correct stickers, secondary barriers and a few cables unsupported . Thanks
 
Nah. I know what you're saying but if someone was clever enough to be thinking about phase rotation they would change rotation at the accessory or load end.

My diagnosis = Numpty.

And what if the incoming supply to the building was in fact L3, L2, L1 rotation and all motors and other phase rotation dependant equipment had been connected to match that configuration?? Still Numpty??
 

Reply to 3 phase breaker in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
496
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top