Hey guys.

My mate is looking at a new compressor for his body shop.

The only thing is, its 3 phase and he only has single phase in the workshop.


Has anyone had any experience with any 3 phase converters? Obviously this would be cheaper than having UKPN come to put a 3 phase supply in.

I'd imagine theres a lot out there, but what one are good, if any, and what ones are not?

The compressor is a 10hp motor!


Any advice would be appreciated.


Cheers
 
My mate needs to buy a new filling machine. The local water mains can only supply 10 litres a second but he needs 30 litres a second. Does he buy a filler than can keep within the limits of the mains or get a machine that can't?

.
 
I'm going to pretend there's only been 2 replies.
Thanks for the useful comments.

I've had a little look into it and can see its going to be an expensive bit of kit.
Would like to know if anyone has had any experience with them.

Cheers
 
Silva is making a very good point albeit using plumbing terms .... converting 1ph to 3ph will have a triple duty approx. on single phase to the rating of the 3ph motor.... you say its a workshop which is only single phase so can the supply handle it and is he ready for the electric bill??? short term it might be cheaper to do this way long term may be cost effective to have 3ph brought in.
 
Thanks, I do see your point. I'm asking as that's what he's asked me to do.
I've not looked much into the converters yet so no idea what sort of supply they need.
The workshop currently has 100a single phase.

I know he's been offered this compressor for a good price, plus I don't think they are available in this size in single phase.

I'm going to call the board tomorrow to get a quote and see what they want.

Cheers
 
100A single phase

Get your mate to ask about getting a 3 phase supply as I have a horrible feeling he is going to add more equipment in the future and that won't be big enough.
 
Hey guys.

My mate is looking at a new compressor for his body shop.

The only thing is, its 3 phase and he only has single phase in the workshop.


Has anyone had any experience with any 3 phase converters? Obviously this would be cheaper than having UKPN come to put a 3 phase supply in.

I'd imagine theres a lot out there, but what one are good, if any, and what ones are not?

The compressor is a 10hp motor!


Any advice would be appreciated.


Cheers

Hi Screech,


I don't know much about 3 phase converters, but i can give advice on different types of compressors like air, screw, compressors where we ordered. want approach them.
 
I don't think it's as big a problem as people are making out. He could use an invertor connected to just the compressor. Am I right in saying 10HP is around 7.5kW? A single phase input invertor would be around ÂŁ600 I would guess.

Single 230v phase input/3 phase 230v output connected to the compressor. So it would have to be able to be connected in delta. A little design of the run signal and it should be OK.

Only issue is the 8kW or so input, around 30 odd amp. It would be like having an 8kW shower running all the time. Obviously it will knock off when the required pressure has been reached.

So a little unconventional but certainly do-able, unless I am missing something.
 
I don't think it's as big a problem as people are making out. He could use an invertor connected to just the compressor. Am I right in saying 10HP is around 7.5kW? A single phase input invertor would be around ÂŁ600 I would guess.

Single 230v phase input/3 phase 230v output connected to the compressor. So it would have to be able to be connected in delta. A little design of the run signal and it should be OK.

Only issue is the 8kW or so input, around 30 odd amp. It would be like having an 8kW shower running all the time. Obviously it will knock off when the required pressure has been reached.

So a little unconventional but certainly do-able, unless I am missing something.
As ive already mentioned and yes your missing something... you convert 1ph to 3ph you triple the demand on the supply now its highly likely he has a 3ph 400v motor and you can get inverters 230v 1ph to 400v 3ph but these again add to the load in comparison to 1ph 230v to 3ph 230v.... this compressor could be taking around 40% to 70% of the supply and duty of the compressor all comes down to what he is attaching to it and given the size of it he has a few heavy pneumatic loads.
 
As ive already mentioned and yes your missing something... you convert 1ph to 3ph you triple the demand on the supply now its highly likely he has a 3ph 400v motor and you can get inverters 230v 1ph to 400v 3ph but these again add to the load in comparison to 1ph 230v to 3ph 230v.... this compressor could be taking around 40% to 70% of the supply and duty of the compressor all comes down to what he is attaching to it and given the size of it he has a few heavy pneumatic loads.

Not sure I follow. What do you mean triple the demand on the supply?

Plus I think the point made is that the compressor motor would need re-linking from star to delta configuration to convert it from 400V 3ph to 230V 3ph.

What am I missing?
 
If you say have a 1ph fixed load of 10 amps it will draw 10amps off the supply, now say you have a 3ph load whether you can use 230v or 400v motor connections and you want to fit an inverter to allow it to run off 1ph then the 1ph supply has to provide power for the electronically generated 3ph all of which will take 10amps per phase in this example so the duty of the motor on the mains would be triple the plate rating .... this would increase if you try to use an inverter that also has to increase the voltage too 230v - 1p in / 400v - 3ph out.
You can't get something for nothing if the inverters were 10amps in 1ph and 10amps out 3ph then they would be called perpetual machines generating 66% more energy out than put in.
 
Not sure I follow. What do you mean triple the demand on the supply?

Plus I think the point made is that the compressor motor would need re-linking from star to delta configuration to convert it from 400V 3ph to 230V 3ph.

What am I missing?

You are suggesting a motor inverter. The largest off-the-shelf one I could find was 2.2kw. Please link us to a 7.5kw one you know of. Or regurgitated manuf. spec of input supply requirements.

.
 

Reply to 3 Phase converter. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

All of the information for MG stuff is freely available from Schneider
Replies
8
Views
768
davesparks
D
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top