I have a 3 phase brook crompton delta motor connected to a direct on line starter, it keeps blowing the mcb, any suggestions as to why this is happening?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 phase delta connected motor advice in the UK Electrical Forum area at ElectriciansForums.net
Electrician wired this unit up and thought it could be the MCB not being motor rated.
You just edited that type (d) lol .... although i got the drift hes out of his depth hence a my advice, im sure my terminology will let him know it isnt as simple as....I don’t think our OP is an electrician so I don’t think we’re going to get much more info.
The O/L’s are set correctly is about the only useful thing I can glean from this.
The best course of action is get the electrician back to do a full set of IR (1000V) and CR tests to prove the motor. Mechanical loading could be a problem but without seeing the machine it’s just a guess.
The MCB could do with being 50A type C
Just one quick question from me.
Why would a loose connection or dodgy crimp trip the MCB?
I must say Marvo i totally supprised by your answer, may i point out the mcb is under-rated for the starting current of a 7.5kw motor, plus the extra duty of it been a plastic crusher (high inertia drum) may even require further allowances, a standard load motor of this size would require a mcb of 50(c) direct or star/delter, and if the ELI can be met a 20A type(d), although the mcb is there to protect from short circuit it still have to allow the start up inrush through without tripping, the overload on the contactor has already got this allowance.The voltage across the windings is different. If your motor's rated at 380 volts then leave it wired delta.
First thing to do as already suggested is the usual basic off-load tests. Do all 3 windings have continuity and do they pass an IR test?
From this quote I'm assuming your not a sparky so you'll need to get him back to finish what he's started. I doubt the 32A MCB is the problem unless it's starting under massive load in which case he'll need to install a star/delta starter.
The 32Amp MCB is there to protect the cable. The DOL starter is there to protect the motor. If the 32 A MCB is tripping before the thermal overload in the DOL starter I'm already suspecting this motor might be heading for the scrap bin.
Unbalanced load draws more curent on the two good phases.
I must say Marvo i totally supprised by your answer, may i point out the mcb is under-rated for the starting current of a 7.5kw motor,......
I would always size the MCB according to the cable it's supplying. With an AC3 or AC4 load I might spec a slower curve to build in some tolerance for start currents especially if there are very frequent stop/starts involved. If the cable size allows you could install a 50Amp MCB.
With a 10 horse motor (assuming 4-pole) a 32 Amp MCB should be more than adequate. If the machine is direct drive with high starting torque requirements then DOL is'nt going to cut mustard.
Reply to 3 phase delta connected motor advice in the UK Electrical Forum area at ElectriciansForums.net