I have a 3 phase brook crompton delta motor connected to a direct on line starter, it keeps blowing the mcb, any suggestions as to why this is happening?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 phase delta connected motor advice in the UK Electrical Forum area at ElectriciansForums.net
....but unless you want nuisence tripping its good practice to follow their guides and works backwards to then weigh up cable sizing etc.
My intention wasn't to surprise you
Yes, from a new design point of view I completely agree, start with the load and it's mode of operation and design backwards to the supply but the installation is already existing in this case so I would be very wary of replacing an existing 32A MCB with a 50 Amp device.
In this particular case the start current of a 7.5kW 4-pole motor should be under the magnetic trip range of the 32A MCB and the run current is under half of the MCB rating so I'm still not convinced the issue is the MCB size unless there's unusual circumstances such as high stop/start frequencies or high start torque requirements which may need a remedy that involves a completely different starting arrangement.
My intention wasn't to surprise you
Yes, from a new design point of view I completely agree, start with the load and it's mode of operation and design backwards to the supply but the installation is already existing in this case so I would be very wary of replacing an existing 32A MCB with a 50 Amp device.
In this particular case the start current of a 7.5kW 4-pole motor should be under the magnetic trip range of the 32A MCB and the run current is under half of the MCB rating so I'm still not convinced the issue is the MCB size unless there's unusual circumstances such as high stop/start frequencies or high start torque requirements which may need a remedy that involves a completely different starting arrangement.