Hi, I have been out to a property 3 times in the past week to a country pile with a 3 phase supply that keeps blowing it's 100amp distributor fuse.

The property has a pool house, a large garage with power, stables with power and a wooden annex type space also with power.

I have taken off every accessory in this huge place and can't find any obvious issues.

At the board I have measured a PFC of 1.19 kA and a PSCC of similar.

Nothing trips in the board when the dist fuse goes, I've not done a lot of work with 3 phase so unsure where to go from here.

Any advice much appreciated.
 
Is there also a washing machine on the "Tumble Dryer" circuit? Just that 40A is large for a tumble dryer on its own, unless it is a commercial unit (which I suppose it could be, at a 6-bed equestrian property). Also investigate what appliances are connected to the 32A ring final on the yellow phase. In fact, run the tumble dryer, water heater and whatever appliances are connected to the RFC with a clamp on the yellow phase and I'd wager you'll find the answer.
 
There are two 32A rings labelled 'laundry' on red phase so I expect the washing machines are on those. 40A is not unreasonable for a big dryer that will take horse blankets, but it looks like a later addition, as is another unlabelled 40A MCB that might be a distribution circuit also on yellow. Blue has the cookers and some water heating, red has more water heating, the laundry and two further rings although not the kitchen one.

I'm kind-of surprised it's eating 100A bullets, I've seen worse load assignment efforts.
 
Just a thought - in the OP, stables and pool house are mentioned, yet there is no mention of these on the visible circuit labelling, although there are some blanks...
Have you confirmed that the three phases come straight into the board pictured and there aren't Henley blocks upstream splitting the red phase to another single phase board you are unaware of, powering outbuildings? When you said it was the red phase burning fuses, this got me thinking, as more often than not if someone also wanted a single phase supply, by default they'd use L1. You can see this at events venues regularly, particularly older installations, where you have a 63/3 with a 63/1 or 32/1 on L1 adjacent.
 
Indeed - it's hard to see how there's enough load on L1 in that board to cause trouble unless all the rings are maxed out. I was thinking the unlabelled 40A on yellow could be a submain to an outbuilding db carrying pool load etc, but red, not so. Only one unlabelled 20A.
 
Using these diversity figures for a hotel I found quickly at:
Calculating Maximum Demand | Voltimum UK - https://www.voltimum.co.uk/content/calculating-maximum-demand-0

Lighting @ diversity of 75%
Heating & Ventilation @ diversity of 80%
Water Heating no diversity
Socket Outlets five 30 A ring circuits @ F.L. 1st circuit & 50% of other circuits

For red phase - maximum demand estimate

64 + 32 + 8 + 1 + 16 + 20 = 141A

3 rfc - 2 laundry and grd floor n02 3 x 32A = 96A
32 + 16 + 16 = 64A

7 lights 6A 7 x 6A= 42A
42 x 0.75 = 32A

1 lights 10A 1 x 10A= 10A
10 x 0.75 = 8A

1 fan convector/shower pump 6A 1 x 6A=6A
6 x 0.1 = 1A

IH 16A 1 x 16A=16A
16 x 1 = 16A

MID con panel boilers 20A 1 x 20A=20A
20 x 1 = 20A
 
Hi,

I returned to the property today, was greeted by the gardener who told me that a couple of weeks ago he found a cable whilst laying some slabs that had tape wrapped around it. obviously I asked him to show me. Tape looks just a couple of weeks old, after disconnecting the tails at the DB in the pool house control room and running a continuity test to prove this was indeed the cable with the mysterious tape around it I then performed a IR and low and behold got a reading of zero between red phase and earth & red phase and neutral.
 
Is the cable actually a dead short because the fuse, if that was all that protected the cable would have ruptured immediately assuming the impedance was low enough which it must have been at some point it must have been.
 
All 3 phases split off to 4 different isolators, one is for the house, another is a 3 phase board supplying the stables, a workshop and the shed they are in, another to the pool heater and finally one to the pool house which has another 3 phase board.

Is this an entirely independent single phase supply, with its own DNO incomer, or is it as I described in post #30?
 

Reply to 3 phase domestic installation issues in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
663
  • Question
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
2K
  • Question
For anyone looking into the same thing I’ve just found a guy who did an experiment to see if this is how the 3 Phase meters counted units and it...
Replies
3
Views
1K
  • Question
so put the main CU on 1 phase, then maybe the outhouse and charger on another. then you have a spare phase to play with if loads are unbalabnced...
Replies
19
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks