Well our OP has just looked back in. Didn't seem inclined to reply.

A question to the OP, "did you seriously think we would defend your actions?"

You took the chance!
 
A weird one but here we go.

I was asked to add a new 3ph circuit into an existing 6 way 3 phase dorma smith D.B. The board had to remain up and running ( not quite meeting the EAWR I know) so with the singles now in all I had to do was slide the 3ph breaker in the spare space 6L1-6L3.... This was where the explosion happened.

Everything was clear of the terminals, the new breaker was, just in case, switched off. As I pushed it onto the bare copper something caused 2 phases to come together resulting in me with temporary blindness, my hand completely black and ending up with me on the floor on the other side of the switch room.

The board and myself were in a bad way but once I was ok I began looking for explanations. The breaker wasn't bridged out which I had expected and nothing obvious stood out in the smoking D.B.
My foreman couldn't explain it either but he had heard of it happening before because of the air in a live board becoming 'ionized' therefore becoming conductive. Any spark caused by the breaker touching the busbar would have been enough to jump through the now conductive ionised air and bridge out to the next phase.

Has anyone else heard or come across this as I'm struggling to find a possible cause

Mark

Stupidity on your part for doing it live in the first place, if you worked for the company I work for you would have been sacked on the spot.

EAWR 14 comes to mind, if this was reported to the HSE expect to be making a visit to the man/lady with a white wig and black gown.

 
I'm gona stick my neck out here and admit that I regularly terminate new circuits onto live DB's. 99% of the time it's MG/shnieder gear but sometimes it's square D. I would refuse to work on some DB's live, if I thought there was danger.
I know I'm taking a risk when doing this, and it's one that I accept. I'm always careful and I understand the risks. Unfortunately shutdowns in my industry are a nightmare to get, and often have to be at midnight for critical plant, which nearly all of the DB's I work on.
As for EAWR, it uses the term "as far as is reasonably practical". This is down to interpretation, and something that lawyers will argue about.
Im happier doing the above work than I am using old ACBs!
 
I'm gona stick my neck out here and admit that I regularly terminate new circuits onto live DB's. 99% of the time it's MG/shnieder gear but sometimes it's square D. I would refuse to work on some DB's live, if I thought there was danger.
I know I'm taking a risk when doing this, and it's one that I accept. I'm always careful and I understand the risks. Unfortunately shutdowns in my industry are a nightmare to get, and often have to be at midnight for critical plant, which nearly all of the DB's I work on.
As for EAWR, it uses the term "as far as is reasonably practical". This is down to interpretation, and something that lawyers will argue about.
Im happier doing the above work than I am using old ACBs!

There's a big difference between terminating a circuit and installing a new MCB, John.
I wouldn't dream of killing a board for connecting a cable.
OK they are a thing of the past but I'd happily conect to open frame boards live, but I was shown how to do it safely.
 
OK they are a thing of the past but I'd happily conect to open frame boards live, but I was shown how to do it safely.
I had a very close call during my apprentiship with one of these boards.I should add, I wasn't working on the board I was cleaning in the sub.
 
Last edited by a moderator:
I include the fitting of MCBs in what I was describing Tony.
As I've said, I look at the job and make a decision on whether I feel I'm happy to do the job. The MG boards are brilliant bits if kit. I don't like SQ D cos I never feel like they make decent contact and they can arc a little of you knock em.
 
At the end of the day John we all know it's up to the electrician doing the job to call the shots. We’re each our own safety officer, never mind what “the management” think.
You’ve been in the game long enough to have influence on and the respect of the idiots that think they’re in charge. I’ll bet you’ve been in the same sticky situations as me where someone has had to put their foot down and say no. It doesn't make you the flavour of the month at the time, but no one can force the issue.
In the space of a week I’ve had a rollicking for working live and one for shutting a plant down. Just accept "you can't win" with them.
 

Reply to 3 phase explosion in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top