davesparks
I suspect the degree of imbalance to cause problems is probably 30% of the total capacity, not 30% of any light load. It is rated around 24A per phase so I would aim for less than 8A imbalance.
No, 30% of the actual loading is what I have always worked to.
The voltage regulators can get very upset if a light load is running imbalanced in my experience.
They seem to be more tolerant of imbalance once they've got a bit of load on them.
I once arrived on an event site to start setting up and found one of the pair of 200KVA generators on and hunting. The site guys had started it up themselves and plugged in a few single phase leads to run their tools, kettle etc, mostly on the same phase.
The cause of the hunting was the AVR having gone kaput likely caused by the unbalanced light loading.
As I said, this is just personal experience so may not be technically correct.