3 Phase heating coil | on ElectriciansForums
Discuss 3 Phase heating coil in the Talk Electrician area at ElectriciansForums.net
ASBTTE
India
Hi. I'm making a 3 phase furnace with heating coils. Total power rating is 5 KW. I have to make one heating element for each phase. How do I split the KW rating? Will it be a straight 5/3? Also when calculating the resistance for each heater, should I calculate based on 220V(single phase voltage in India) or 440V (3 phase voltage)?
Yes, that is correct
you must firstestablish whatvoltage teach coil requires.if it's 230V per coil, then 415V is :
In delta each coil would be 5000/3 = 1666watts.So res of coil would be v squared/watts = 440sq/1666=116ohms per coil.If you say the single phase v is 220,3 phase should be 380v not 440v,unless its a wierd system.
Regards,S
Reply to 3 Phase heating coil in the Talk Electrician area at ElectriciansForums.net
Hello All, This is Vaithees from India. We are using an IR heater for a vacuum & non-vacuum chamber and got a heater from Chinese company and its...
As long as the heat input is greater than the heat losses from the container and the resistance is sufficient to limit the current to no more than...