A customer has asked me to install a supply for a Wenger Webcot kiln.

The faceplate is very worn and I cannot see the kW. They state the kiln it type 3670w and is rated at 12kW.

The paperwork does have 3670w on it but when I look at the spec sheet (see picture 2, SpecSheet) ) there is no sign of a kiln which is 12kW. This model has 12 elements therefore it must be one of the last 6 models on the spec sheet, but again no sign of 3670w. It looks like there is one called 3060w though but this is not 12kW. Does anyone have any ideas how I could find the kW, or does anyone recognise the kiln details and know the kW?

The wiring diagram (see picture 4) shows that it can be wired as single phase or 3 phase. This will be wired as single phase. My questions...

1. Do I just join the 3 phases together as per the diagram?
2. Do I need to increase cable size compared to the existing flex on the Kiln as I am joining 3 x 10mm cables into one conductor? Although the neutral carries the same current and there is only 1 neutral conductor! Why is this?
3. On the spec sheet (pic 2) it has 2 columns for electricity supply required. One for single phase and one for 3 phase. The last 4 columns for single phase have a dot. looking below it says treat as nominal rating 14kW for single phase, yet the actual column labelled nominal electrical .loading states different, higher values, why is this?

Pictures below show the almost unreadable faceplate, spec sheet, cable and part of the wiring diagram.

Picture 1, faceplate.
(1)faceplate.jpg

Picture 2, Spec sheet.
(2)Spec sheet.jpg

Picture 3, Cable
(3)Cable.jpg

Picture 4
(4)3P or SP.jpg
 
Group reading

L1 to L2
L1 to L3
L2 to L3

Each reading should be more or less the same.

Take this common value and divide by 4 then use basic ohms law.

I = V/R
Amps = 400/resistance.

Single element reading - resistance of single element (wiring disconnected)

Pick your voltage either 230 or 400, ideally 400 as that is the supply you are connecting.

Amps = 400/resistance of one element.
This is where I'm getting confused.

You say Amps = 400/resistance of one element

Therefore Amps = 400/3.3 = 121A.

The other examples show that an element with 3.3 ohm of resistance indicates 12kW of power which is 52.2A

i.e. 3.3 x 4 (elements) = 13.2 ohm p/set of elements.

230/13.2 = 17.4A per phase = 52.2A for all 3 phases.
 
My bad, @happyhippydad

You are been told a few differing methods here and I threw confusion into the mix, I edited that post to allow a star config of both single and 3 phase, you quoted it before the edit.
I actually posted wrong, I posted a job I am doing atm which is another config so apologies for the confusion here.
 
You don't have 400v across each group of elements you have 230v whether the supply is 230 or 400v.
Depends on where exactly you are testing from an what tests, if you are testing from the output of the contactor then you are measuring 8 elements between 2 phases (400v)
If you are testing from the output of the contactor to any PH / N then you have a group of 4 (230v)
If you are testing at the elements then it again depends on where your testing points are whether to apply 230v or 400v but crucially as I think you were saying - 1 group of 4 elements will not have 400v applied to it which I agree fully with.
 
This has been very interesting. Thank you all for helping me understand it better.

Just to make sure I'm getting it...

Lets say I measure the resistance of 1 of the elements and it is 2 ohm (we'll assume this is correct for all of them). To find out the power rating of the kiln we would do the following:

2 ohm x 4 = 8 ohm p/set of elements.

230/8 = 28.75A p/set

x 3 = 86.25A for all 3 elements.

x 230v = 19.8 kW (to 1 dp)

Is this correct?
 
Is this correct?

Yes.

One thing that deserves explaining here is the actual connection configuration of the element groups. We can ignore that each group is actually made of four physically separate sections and just consider them as single elements.

Each element group is connected from one line terminal to neutral (via the main switch and contactor.) In other words the kiln contains three identical, single-phase 230V heaters, just like three fanheaters sat on the floor with separate flexes and plugs. It wouldn't matter whether you plugged those fanheaters into three sockets on the same phase, or three sockets on different phases, because they are independent. Same with the kiln - the three line terminals can be connected to the same phase or different phases, so long as each terminal is 230V from neutral.

This is a different situation to (e.g.) a 3-phase motor, which is not like three independent single-phase motors because the magnetic fields of the three windings interact with each other. The windings must be connected to alternating voltages that vary in time with the correct phase relationship to each other. You cannot simply connect all three to one phase.

Likewise, a different situation obtains in a heater consisting of three identical elements connected in star (i.e. each between a line terminal and a star point) but where the star point is not connected to the supply neutral. This is a handy configuration for industrial supplies where a neutral might not be available When connected to a 3-phase 400V supply, the three elements form a balanced load in which each element receives 230V between the line terminal and the star point. Through symmetry, the star point will lie at a voltage close to that of the supply neutral, hence the element currents and voltages would be just like those of the klln (although note that the 230V control ccircuit of the kiln absolutely requires the neutral to be present). But clearly, if the star point of our heater is not connected to neutral, wiring all three line terminals to the same phase won't work because now there is no complete circuit. Like the motor, this needs a 3-phase supply.

Returning to the kiln and considering the currents in the circuit conductors; on 3-phase the currents from the three elements sum to zero at the neutral terminal (except for the small control circuit load) unless one element fails O/C in which case the neutral current will equal the line current. On single phase the line and neutral currents are inherently equal. The line and neutral currents can be taken as equal both on single-phase and 3-phase supplies, with the current on single phase supply three times that on 3-phase.

What I hope to have shown in the above explanation is that the kiln elements, by virtue of being connected L-N, are less like a 3-phase load and more like three single-phase ones, for which ordinary single-phase calculations can be applied.

You can supply your own sketches to accompany the above :)

Oh, BTW
230/12000 = 0.0192ohms

R=V/P ???
For this, you are to beat yourself with a big lump of SWA until it really hurts.
 
Last edited:
Yes.

One thing that deserves explaining here is the actual connection configuration of the element groups. We can ignore that each group is actually made of four physically separate sections and just consider them as single elements.

Each element group is connected from one line terminal to neutral (via the main switch and contactor.) In other words the kiln contains three identical, single-phase 230V heaters, just like three fanheaters sat on the floor with separate flexes and plugs. It wouldn't matter whether you plugged those fanheaters into three sockets on the same phase, or three sockets on different phases, because they are independent. Same with the kiln - the three line terminals can be connected to the same phase or different phases, so long as each terminal is 230V from neutral.

This is a different situation to (e.g.) a 3-phase motor, which is not like three independent single-phase motors because the magnetic fields of the three windings interact with each other. The windings must be connected to alternating voltages that vary in time with the correct phase relationship to each other. You cannot simply connect all three to one phase.

Likewise, a different situation obtains in a heater consisting of three identical elements connected in star (i.e. each between a line terminal and a star point) but where the star point is not connected to the supply neutral. This is a handy configuration for industrial supplies where a neutral might not be available When connected to a 3-phase 400V supply, the three elements form a balanced load in which each element receives 230V between the line terminal and the star point. Through symmetry, the star point will lie at a voltage close to that of the supply neutral, hence the element currents and voltages would be just like those of the klln (although note that the 230V control ccircuit of the kiln absolutely requires the neutral to be present). But clearly, if the star point of our heater is not connected to neutral, wiring all three line terminals to the same phase won't work because now there is no complete circuit. Like the motor, this needs a 3-phase supply.

Returning to the kiln and considering the currents in the circuit conductors; on 3-phase the currents from the three elements sum to zero at the neutral terminal (except for the small control circuit load) unless one element fails O/C in which case the neutral current will equal the line current. On single phase the line and neutral currents are inherently equal. The line and neutral currents can be taken as equal both on single-phase and 3-phase supplies, with the current on single phase supply three times that on 3-phase.

What I hope to have shown in the above explanation is that the kiln elements, by virtue of being connected L-N, are less like a 3-phase load and more like three single-phase ones, for which ordinary single-phase calculations can be applied.

You can supply your own sketches to accompany the above :)

Oh, BTW


R=V/P ???
For this, you are to beat yourself with a big lump of SWA until it really hurts.
Interesting point about connecting as star with no neutral.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
3 phase kiln questions?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
60
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
HappyHippyDad,
Replies
60
Views
8,321

Advert

TrueNAS JBOD Storage Server

Back
Top