Hi all I was called to a job this morning where the 3 phase supply was showing low voltage on two phases? The voltages where L1-245v
L2-110v
L3-135v
could anybody give any possible reasons why this was the case? I have handed it over to supply company as I thought must be a fault on their side
thanks for any input.
Ok, which side of the isolator and was it closed or open? What was the voltage to earth of each phase and the voltage between phases?
Yes in uk. PME Earth at source TT at consumer side
showin 415v (approx) between L1 and L3
235v (approx) between L2 and L3
Same between L1 and L3
Presumably you meant to say 235 between L1 and L2? In which case I'd be inclined to say that the fault is indeed external and that it is on the L2 supply, possibly a high resistance connection, or something more sinister.
Sorry Dave yes your right I did. I was leaning towards the L2 fault as well, Scottish power on site now so hopefully some answers shortly.
Reply to 3 phase low voltage?? in the Talk Electrician area at ElectriciansForums.net
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
To show the varying line voltages you can plot it as a phasor diagram then use Millmans Theorum to calc the voltages wrt supply neutral. There's...
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...