Hi all I was called to a job this morning where the 3 phase supply was showing low voltage on two phases? The voltages where L1-245v
L2-110v
L3-135v
could anybody give any possible reasons why this was the case? I have handed it over to supply company as I thought must be a fault on their side
thanks for any input.
 
Ok, which side of the isolator and was it closed or open? What was the voltage to earth of each phase and the voltage between phases?
 
Yes in uk. PME Earth at source TT at consumer side
showin 415v (approx) between L1 and L3
235v (approx) between L2 and L3
Same between L1 and L3
 
Presumably you meant to say 235 between L1 and L2? In which case I'd be inclined to say that the fault is indeed external and that it is on the L2 supply, possibly a high resistance connection, or something more sinister.
 
Sorry Dave yes your right I did. I was leaning towards the L2 fault as well, Scottish power on site now so hopefully some answers shortly.
 

Reply to 3 phase low voltage?? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
309
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
290
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
729
  • Question
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
Replies
1
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top