Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?
 
Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?

Three Phase Current - Simple Calculation
 
Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?

I don't know what you are trying to calculate there but if the data plate says 12.4A then that is your design current.
A 16A mcb seems appropriate.
I cannot comment on cable size as you have not provided enough information, but at a guess I'd assume 4mm until further information is provided.
 
Do you know if the supply was put in for the current dishwasher?

It may be the original installation was for a larger more powerful dishwasher.
This may have been downgraded and now they've found out it's too small and need additional capacity.
 

Reply to 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top