The company I work for sent out some guys to connect up some temps through a 3 phase meter. Now the circuit was fed via an existing board with a 63A breaker and the existing board was backed up by a 160 amp mccb.(plus an rcd for the sub-main). The 3 phase meter so I have been told went up in smoke on 2 occasions and took out both breakers.
On the 3rd occasion I was sent to check it out. I found 2 phases reversed at db ie brown and grey connected wrong way around and I found brown phase to be carrying 96A and other 2 phases about 35A . I put everything right with phases and balanced loads so all were carrying about 50A. (Also existing meters were direct connect.) All I wanted to know is if anyone knew which of these faults would cause the meters to burn out?
I thought if phases were reversed it would just cause the wheel to clock backwards and also thought meters would carry 100A fine. Thanks for any info.
 
I've never seen a metering unit that could be damaged by phase reversal. A make and model number for the meter would help so we can look for an on-line datasheet.

I assume this was direct on-line metering, not CT metering. Most likely terminations or possibly a highly inductive or capacitive load if it's an industrial installation.
 
I’ll go along with Mavo (but not if he’s wearing that outfit, I do have standards). Reverse phases won’t make any difference. It could only be load or poor terminations. As most meters are designed to withstand a reasonable amount of overload then I’d look at the terminations.
 
Hi Gang , sorry to interject and change the subject slightly , however have been asked to fit a 3 phase meter in an industrial / commercial unit . The meter is going to be situated adjacent to the tennants DB so they know the landlord is not ripping them off . My question is , do i need to fuse the CT's if so i have read that the fuse must go before the CT , how is this possible if we are unable to remove the incomers from the dB due to their work load in unit . I know i can use split CT's but just wondering about the fuses
 
You should start a new thread not resurrect an old one. This was dead and buried.

You can get shell type CT’s (in two halves). BUT do not fit them with the board on load! (Unless you’ve got a death wish). Select your time, lunch break, shift changes or night time.
 

Reply to 3 phase meter in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
450
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top