3 phase motor intermittantly tripping | on ElectriciansForums

Discuss 3 phase motor intermittantly tripping in the Talk Electrician area at ElectriciansForums.net

Joined
Sep 24, 2012
Messages
1
Reaction score
0
I have got a 3 phase motor running a conveyor belt, every couple of days it will trip the overload. I have tested the motor, windings are ok, not drawing excessive current, good insulation resistance. It has a brake mounted on it but this seems to be releasing ok.
Motor does get a bit hotter than the 2 conveyor motors next to it.
any ideas
 
What is the flc of the motor?
What are the overloads set at?
How it it wired DOL or SD
How is the motor configured Star or Delta?
 
Intermittent problems are the hardest to find. could be as said above.
Do the basic things first
Check the belt runs freely no stiff bearings or badly tracked belts.
Clean the fan, cowl, and motor casing so it can cool correctly.
Check condition of any remote isolator and the actual contactor loose, dirty or pitted contacts can cause intermittent phasing and overload. Also check and test cable condition.
Use a clamp meter to check the current draw each phase.
Do you know if its tripping on start up or after its been running for a while?
 
What material are you conveying? If the environment is dusty or damp, or the faulting conveyor is used more than the others, you may have to up the PPM on that asset. Overloads generally set at 5/8 FLC or 65% ish, if its already been cranked up there may be much knee work and head scratching.
 
If the current, load, load frequency, and environmental are same as other two motors. You confirmed all wiring. you could be seeing the results of a past problem. Like a previous load issue over heated motor and caused insulation failure, or contractors worn from past problem. Basically I am reminding you to consider, past abuse may have have caused degradation which now presents itself to appear as intermittent problem when it is really an accumulative issue. Ringing it and use a scope may help verify.
 
What material are you conveying? If the environment is dusty or damp, or the faulting conveyor is used more than the others, you may have to up the PPM on that asset. Overloads generally set at 5/8 FLC or 65% ish, if its already been cranked up there may be much knee work and head scratching.

Only if the motor is YD and the overload is in the delta leg.
 
Common practice in the states, and when the cores get too big for fire nuts:
[ElectriciansForums.net] 3 phase motor intermittantly tripping


View attachment 35874

View attachment 35875
 

Reply to 3 phase motor intermittantly tripping in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
381
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
776