The conveyor jams because of the nature of the product. It's just high volume food belting down the line and unless someone just stands there and polices the line all day, jam-ups will happen. I will be able to install the Inverter myself, I was just trying to see what you guys would do in a similar situation.
 
Hi Darkwood,
You might have misunderstood me.
We use MCB's and motor overload / protection devices.
Not just a MCB to protect the motor. The whole design is carefully done to match the motor to the mech. drive unit. We always!!! use motor overload devices whether it be thermal / electronic overloads. Depending on the application we would consider whether to use thermal / electronic or even vsd's.
We tend not to overdesign as cost is important. What i tried to say is that you should start with the MCB sizing as this gives a "degree" of protection. If your application is wrong, where your motor might be too powerfull for the application you should solve this first. We start and protect 0.55Kw to 2500Kw motors in our plant. I presumed having a overload device in the starter came without saying!!

Working in a plant with about 2000 motors we regulary have either conveyors and or pumps jamming. Where there are thermal overloads fitted we never have damage as the MCB always trips. I agree the MCB alone is def not an ideal motor protection device. When you have a steady overcurrent over a long period of time the MCB won't trip, that is the job of the overload device.

Thanks :)
 
Hi Guys,I am getting the same reply to a thread(3ph Overload problem) twice a week with no new content.Does any one know what im doing wrong?
Roy
Quadrant
 
Hi Darkwood,
You might have misunderstood me.
We use MCB's and motor overload / protection devices.
Not just a MCB to protect the motor. The whole design is carefully done to match the motor to the mech. drive unit. We always!!! use motor overload devices whether it be thermal / electronic overloads. Depending on the application we would consider whether to use thermal / electronic or even vsd's.
We tend not to overdesign as cost is important. What i tried to say is that you should start with the MCB sizing as this gives a "degree" of protection. If your application is wrong, where your motor might be too powerfull for the application you should solve this first. We start and protect 0.55Kw to 2500Kw motors in our plant. I presumed having a overload device in the starter came without saying!!

Working in a plant with about 2000 motors we regulary have either conveyors and or pumps jamming. Where there are thermal overloads fitted we never have damage as the MCB always trips. I agree the MCB alone is def not an ideal motor protection device. When you have a steady overcurrent over a long period of time the MCB won't trip, that is the job of the overload device.

Thanks :)
Was just a short post you put and it gave the wrong impression but your obviously putting all this into the design, sorry for the mix up but not everyone is fluent in motor control and protection but obviously you are.
 
I think you are correct to go for an invertor.

Overloads are supposed to be coarse enough to avoid tripping on start up and short heavy loads.

I had one on a conveyor recently that was tripping after about 30 seconds. It was set at 4 amps, as the motor plate stated but was actually taking 15amps. The cause was that it had been wired in delta instead of star. So it was taking that long with almost 400% overload.

I usually use Allen Bradley powerflex 4 invertors. Dead easy to get hold of, wire up and program. You can select the current to be displayed so you can watch what it takes on normal loading. You can then set the overload trip current accordingly.
 
Cheers,

Just wondering, the motor has a gear box so it is running at a low speed with high torque. So there is quite a lot of power going through it. Will the Inverter do its job - i.e. cut out the motor when a fault current is detected?
 

Reply to 3 Phase Motor Overload Problem? in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
367
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top