Hi i have recently reconected a 3 phase fan at my workshop its rotation is correct but it now gets very hot any suggestions?
 
Hi,
If the current on each of the three phases is uneven, the polarity of the windings may
be incorrect? ..or you may have connected the motor in the delta configuration instead
of star (6 terminals on motor?)
 
[/b]

wouldn't this cause tripping on start-up ?

Depends on what starter you were using!!;)

What is the KW rating of the motor??

Has it got DOL, Star/delta, soft starter, invertor etc for starting?

Is it squirrel cage, wound rotor, reaction etc etc

Some more details would be nice, take a look on the rating plate if you are not sure
 
I agree with what has been said already, sounds like motor is connected in delta. On a standard cage 400/230 3ph motor this means that 400v are across a 230 winding, on a small motor it will start up no problem in delta just it will over heat and eventually fail. Or you could be using a non standard winding like 380/200, really need more info from motor plate/start control.
 

Reply to 3 phase motor wiring in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
381
I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top