3 phase motor wiring | on ElectriciansForums
Discuss 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net
Lincs
Hi just after some advice on how to wire this water motor. I have follwed the wiring diagram, when I test it, just get a buzz from the motor, Not spinning at all. Tried switching line conductors, same result.
Supply is 3 phase & Neutral.
[ElectriciansForums.net] 3 phase motor wiring
diss. the control circuit cables. then try pressing the contactor in manually. if it fires up then, you have a control circuit fault/incorrect wiring/incorrect coil volts.
When a motor won't run, always worth checking that all phases are present i.e. 400V between them and 230V to N or E, before anything else. Would have picked up the starter wiring error instantly. If all OK, then usually it's a miswire of the motor leadouts.
You may have already damaged the motor windings by running it on 2 phases, disconnect the cable and test the motor windings for continuity resistance and IR @ 500v.
What is the rated run current on the motor info plate? 9 Amps setting on the thermal overload looks high for that motor but sometimes photos are decieving.
Sounds like a suck it and see scenario, to me.
Messing about with 3 phase motor supply and control can be very dangerous without the necessary experience.
If you're qualified, you're misreading a very basic situation.
If not, you shouldn't be touching this.
Reply to 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...