3 phase motor wiring | on ElectriciansForums

Discuss 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 4, 2017
Messages
7
Reaction score
9
Location
Lincs
Hi just after some advice on how to wire this water motor. I have follwed the wiring diagram, when I test it, just get a buzz from the motor, Not spinning at all. Tried switching line conductors, same result.

Supply is 3 phase & Neutral.

Thanks

[ElectriciansForums.net] 3 phase motor wiring


[ElectriciansForums.net] 3 phase motor wiring


[ElectriciansForums.net] 3 phase motor wiring


[ElectriciansForums.net] 3 phase motor wiring


[ElectriciansForums.net] 3 phase motor wiring
 
diss. the control circuit cables. then try pressing the contactor in manually. if it fires up then, you have a control circuit fault/incorrect wiring/incorrect coil volts.
 
When a motor won't run, always worth checking that all phases are present i.e. 400V between them and 230V to N or E, before anything else. Would have picked up the starter wiring error instantly. If all OK, then usually it's a miswire of the motor leadouts.
 
You may have already damaged the motor windings by running it on 2 phases, disconnect the cable and test the motor windings for continuity resistance and IR @ 500v.

What is the rated run current on the motor info plate? 9 Amps setting on the thermal overload looks high for that motor but sometimes photos are decieving.
 
Sounds like a suck it and see scenario, to me.
Messing about with 3 phase motor supply and control can be very dangerous without the necessary experience.
If you're qualified, you're misreading a very basic situation.
If not, you shouldn't be touching this.
 

Reply to 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
382
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top