Is it allowable to take a 230v supply out of a 3 phase motor connection box, taken off one phase and a neutral?
 
3 phase motors usually have a nuetral supplied if it has a brake usually a 230 v dc is there a rectifier inside the motor connections and has it got a brake fitted
 
Sounds to me like you want to use one of the phases of the motor supply + neutral to run another circuit for something else.....if so I would say no, it's a bad idea. Motors are usually supplied via a protective device. Using the motor supply for an additional circuit will cause havoc.
 
won't be suitable alright-as the motor is prob closely protected by overload

voltage at the motor terminals could drop a fair bit at startup as well-down to 80-85% and might affect whatever you're branching off for
 
overload, unbalanced phases, buggered motor, should be fun. so it's a no from me as well.
 
similar to pmac above... I've seen this method used on a conveyor system where a 240vac solenoid is connected to a phase and star point, for a lube system.
 
In what circumstances would a heater be required within a motor??

I must admit that i haven't to my recollection come across such a circumstance. The only exception has been in compressor units where a heater is employed to keep the refrigerant in a gaseous state....
 
We have several motors with internal heaters varying in age from 40 years down.........some are in pretty damp nasty places too!!! still over 200Meg on the IR test though!!!!!!
 

Reply to 3 phase motor with neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
507
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
484

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top