3 phase problem after spark did 5 year safety inspection | Page 4 | on ElectriciansForums

Discuss 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 23, 2023
Messages
40
Reaction score
2
Location
Liverpool
Hi lads 5 year safety inspection the spark put the tails back and later line 2 of the 3 phase blew blowing the box off the wall and taking out the main fuse on the same line into the building can you all just say quickly what you think the spark may have done wrong ?
Cheers
[ElectriciansForums.net] 3 phase problem after spark did 5 year safety inspection
 
Last edited by a moderator:
OK, but your loads presumably have not changed prior to now, so just measure the load now.
A pic of the SP board breakers may give a clue to whether overloading the board is even possible.

It was rather naughty to not leave the isolator with you, however you still have the board and clamp. ;-)
 
Yes 100% he took them out and put them back in again
Certainly not a standard thing to do on an inspection.

When you do the 2391 (inspection and testing) you are told to disturb as little connections as possible to ensure you don’t create faults.

It’s highly unlikely that the electrician would have removed the tails and reterminated them on an EICR (inspection)

Also, the picture you’ve posted looks like a single phase main switch?
 
An overloaded board but it's run fine for 5 years and it just happend to blow a few hours after they wiggled the wires plus each phase is perfectly balanced with 9 feeds
So he didn’t remove the tails? But wiggled them?
Sounds more likely that there’s been a problem hiding there for a while either from a loose connection causing the cable to overheat and eventually melt into the clamp or the wiggle has exacerbated a defect already there and with a little load on the cable the cable moves and boom.

Also re the overload; It is certainly possible that an overload has occurred even if it has been running fine for years. An overload of a small magnitude can be enough to heat the cable past its operating temperature and cause it to significantly expand, then upon cooling and contracting loosen the connection. Rinse and repeat for 5 years and you certainly could have a situation like this.

I see it all the time where a shower installed on a 6mm cable ran through insulation in a wall and then under loft insulation is used to power a 9.5kW shower and due to the overloading of the cable (which should have been derated due to the insulation) burns out at the terminations of the switch or the MCB or the shower.
Genuinely, funnily enough it usually takes around 5 or so years of normal use for the problem to come to light by which time the spark that put it in is long gone.
 
Last edited:
I don’t think the clamp is the source of the problem it would of been in a dam sight worse condition if it was

I’d say a loose connection that has eventually caused the internals to short

To be honest the whole design of l2 to be loaded up like that is a sh!t show
Another 3 phase db instead and sockets spread across the phases

It’s easy to sit there blaming the spark who could easily of been anyone one here with ought knowing the full circumstances

The biggest thing that stands out to me is he used the tail clamp what puts him/her above 60/70 %of the butchers that get away with it week in week out
 
Good morning. If the cooling system fed by the 3P db did indeed have three phase 3 wire motors, then even though the main L2 fuse ruptured the site‘s L2 conductors would remain energised because it is connected by the motor windings to L1 and L3. The voltage of L2 with respect to N will depend on the L2 load impedances and that of the motors. The current in L1 and L3 will increase as the 3 phase motors run in single phase mode. The motors would not start with only L1 and L3 but they can continue to spin if they were already and a phase was lost.

What happens to the 3-Phase Motor When 1 Out of 3 Phases is Lost? - https://www.electricaltechnology.org/2021/11/what-happens-to-the-3-phase-motor-when-1-out-of-3-phases-is-lost.html

Thus even though L2 fuse ruptured further damage to equipment loads may have happened using current drawn from L1 and L3. What if anything happened to isolate all electricity ie disconnect L1 and L3?

Where the servers fed by UPS and/or voltage regulators?

I concur that the original short circuit was caused by a failure of the termination and squashing of the cable by the clamp. But can see how L2 may have remained energised and significant current might still flow causing further damage.
 
Last edited:
They probably
They probably
So he didn’t remove the tails? But wiggled them?
Sounds more likely that there’s been a problem hiding there for a while either from a loose connection causing the cable to overheat and eventually melt into the clamp or the wiggle has exacerbated a defect already there and with a little load on the cable the cable moves and boom.

Also re the overload; It is certainly possible that an overload has occurred even if it has been running fine for years. An overload of a small magnitude can be enough to heat the cable past its operating temperature and cause it to significantly expand, then upon cooling and contracting loosen the connection. Rinse and repeat for 5 years and you certainly could have a situation like this.

I see it all the time where a shower installed on a 6mm cable ran through insulation in a wall and then under loft insulation is used to power a 9.5kW shower and due to the overloading of the cable (which should have been derated due to the insulation) burns out at the terminations of the switch or the MCB or the shower.
Genuinely, funnily enough it usually takes around 5 or so years of normal use for the problem to come to light by which time the spark that put it in is long gone.
Sorry I was being flipent there he did remove the tails and put them back in the day before the outage
 
MFS makes an interesting point, i cannot recall needing to remove tails from an isolator to do an EICR, plus if they are connected to the Henley rather than a CB off the TP board, they would have been live unless the main fuse was pulled or there is another TP isolator for the whole supply. If you have the ECIR report it will tell us how the board is connected to the supply. I am wondering if he was getting poor readings when testing to the isolator terminals and removed the cables to work out why ?

Anyway, plenty of theories, which do not appear to have a way forward without some evidence to rule in or out various possible causes
 
MFS makes an interesting point, i cannot recall needing to remove tails from an isolator to do an EICR, plus if they are connected to the Henley rather than a CB off the TP board, they would have been live unless the main fuse was pulled or there is another TP isolator for the whole supply. If you have the ECIR report it will tell us how the board is connected to the supply. I am wondering if he was getting poor readings when testing to the isolator terminals and removed the cables to work out why ?

Anyway, plenty of theories, which do not appear to have a way forward without some evidence to rule in or out various possible causes
Morning the best evidence I can produce is that we had perfect balanced system un stressed working well and a few hours after someone did work on it the system failed I do have a video of the electrician who came the next day to rectify on the phone to the office saying "it looks like we've nipped the outer casing when we put it back" and her boss saying is the main fuse that blew on the same line as the breaker......they know they've balls'up but that'd why I so great full to you guys as I'm not an electrical engineer and they are trying to lead me by the nose to bankruptcy
 
That single phase board doesnt appear to be fed by the three phase board, so at some point L2 looks to have been loaded up, or loose, with the visible heat damage there, but is possibly un related, theres just so many unknows here for us, which board are you saying blew off the wall? If you could post the report on here with the inspectors details redacted that may help, but im not so sure. You mention data loss, was there no off site backups? Or ups? Or anything to alert you to the supposed high temperatures in that area by the fans not working? I may have detsils mixed this threads getting a bit long now
 
How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?
 
Morning the best evidence I can produce is that we had perfect balanced system un stressed working well and a few hours after someone did work on it the system failed I do have a video of the electrician who came the next day to rectify on the phone to the office saying "it looks like we've nipped the outer casing when we put it back" and her boss saying is the main fuse that blew on the same line as the breaker......they know they've balls'up but that'd why I so great full to you guys as I'm not an electrical engineer and they are trying to lead me by the nose to bankruptcy

How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?
Hi its our job to have precise amps distributed to our servers so we take a great deal of effort to get it bang on the lid was on the floor and covered in black soot when we went in as was the entire board with heat marks all over
 

Attachments

  • [ElectriciansForums.net] 3 phase problem after spark did 5 year safety inspection
    Screenshot_20231224_221248_Gallery.jpg
    189.9 KB · Views: 65
How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?
Also this is a local authority building so the electricians are paid in a way that anyone who's got a local authority contract will understand its in their interest to have everything undone and redone and they also then get the gig to do any remedials and this is done on the nod a couple of photos to the Borough electrician and help yourselves lads look forward to your invoice
 

Reply to 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
That explanation would make a lot of sense and would certainly explain the new bases and new boxes, with old relabelled alarm heads. I do remember...
Replies
5
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top