Is the generator supply fused?
If the original cable fault took out only one of the supply fuses then the two remaining phases might have damaged one of the motor windings.
Disconnect the motor and test it for winding resistance. Remove any links and megger test between windings if you can as well.
The pump motor is almost certainly damaged but before you reconnect after repairs or replacement make sure it has effective protection against two-phasing.
Good thinking Ill put in place a phase detection relay if there isn't one already, I'm thinking there isn't. Once its lifted out ill test more effectively, my welly boots just aren't made for wading through the water to get to the pump.
With mine pumps we always get a crane to drag it/lift it onto dry ground. Quarry pumps would be similar.
I witnessed one of the maintenance guys on a mine get killed whilst working on a pump in a slurry pit one time so think safety and not just electrical safety, assess and manage risks from all places, especially upstream.
Thanks for the reply Alan wasn't been funny in any way but knowing the sequence of events can save many a guess work and hopefully give better advice
Didn't take any offence from it, I love learning and find asking a forum of highly qualified and experienced people is better than just trying to muddle through it. Means I can learn different safe techniques and methods to get the result I'm after and to improve the safety. I'm not the most experienced but I'm getting there, slowly but surely and safety is paramount in this line of work.
I appreciate all the replies and the patience trying to understand what I'm trying to ask.
Just from a learning perspective, how do you test a motors windings? what results are you looking for?
If you can remove the links you'd test that all three windings are equal resistance and that their resistance is per manufacturer spec if info is available. You'd also megger test between each of the 3 windings to ensure there is no breakdown of the insulation between them.
Test the windings to earth using an insulation resistance tester. Test between each line to earth and expect quite high readings, over 1M ohm is acceptable but I wouldn't like to walk away from a motor knowing the motor is close to that. Then remove links and go between each line and test for resistance and make sure the windings are balanced.
Went in yesterday morning and disconnected the pump from the circuit and tested the cables again for insulation resistance and all OK. Got the quarry operative to start it up, with the pump disconnected, and it didn't trip. Tested voltages and all were fine. So pump at fault. Didn't get a chance to get at the pump as the crane lifted one out and dropped a new one in and the old one was whisked away for repair. When it returns I'll ask what the fault was as I would like to know.
Thanks for all the help and advice.
It had a winding out, so was 2phasing when when you fired it up from what you put, I think we all picked up on that early on when you explained things, what I don't understand is the 'guy' you said had left this to you because he was elsewhere, (I understand you're on your ladder of learning so aimed at him) this was a basic test procedure and he got it wrong, I think if he cannot nail a basic one like this then he shouldn't be undertaking the work in the first place, It makes me wonder if he's trying to do engineering work off the back of his 17th quals and no formal electrical engineering training or any specific motor diagnostic and repair knowledge at least your training in the correct area for this stuff .... some questions need asking here when you see him next as this has cost the company that runs the site extra down time, it may not be an issue on this site but any other it could be a production hit in the thousands of pounds?
We are always happy to help out but your colleague should have easily diagnosed this one with the correct basic test procedures, have a chat with him next time you see him and please explain to him what was wrong and enjoy taking the credit at his expense ;).
Belfast
3 phase quarry pump
Talk Electrician Forum
alanmcm,
timbobelfast,