Hi everyone, each leakage question here.
I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and traditionally have 2/3mA leakage per panel.
So we generally have a 63A three phase distro with a 300 mA on input and multiple outputs protected by 30 mA RCBOs. This is standard video industry stuff. For bigger systems we use 125A at 500 mA.
My question is, when I have to use a 32A three phase supply, it has to have a 30 mA RCD on input, can I pull up to 20/25 mA leakage on each phase, or is the 30 mA trip cumulative, so if I have 10 mA leakage on each phase, will it trip?
So I'm asking, can I get 75 mA leakage out of a 32A three phase supply, like I would with three separate 32A single phase supplies, with an RCBO on each?
Thanks in advance.