ive a 3 phase static inverter with a 4 pin no Neutral power output 420 v. Is it possible to use the 240v power source Neutral on the inverter, change the socket output to 5 pin and use the input power source Neutral as in effect a slave Neutral. The Neutral will not be connected to any wiring in the static inverter only the new socket ?
 
I would offer some caution here, research needed. I’m thinking of the isolation (separating supply and output), these shouldn’t be joined. They are not the same and wouldn’t be common. See Delta vs Star vs delta + Star connections (the latter will have a neutral output). My understanding (and it’s a long time ago) was also the issue of phase harmonics induced in the ‘new’ neutral would make it unstable, I suspect there is good reason there is no neutral on the output (probably price). Overriding the original design may bring bigger problems - be careful what you wish for.
 
Most inverters or converters from a single phase source enable a three phase output with no neutral because it generally is not required. As above the manufacturer would give accurate guidance but connecting a through neutral from the source will not work as how do you intend this neutral not to be connected to the inverter as they are the same thing, I cannot see how this neutral would function.
 

Reply to 3 phase Static inverter Without a Neutral in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
529
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
779
  • Question
The only way to really tell is take an actual amp probe and check it that way. I wouldn’t always depend on your UPS display. You do need a more...
Replies
1
Views
634

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top