Only other thing to mention is what stop the motor riding up too far and jamming (not in a bob marley sense) or damaging the ramp, is there a physical disconnector of the motor like a 3phase lever switch or is it a limit switch to be tagged into stop circuit, sounds doubtful for the latter as its got 400v control and really should have a lower voltage exporting out to limit but nothing supprises me any more with old dodgy machinery.
So as a recap... we have a contactor Dol with no overload protection a 400 3phase flex to motor missing adequate mechanical protection and uncertainty over the safety system if one exists of the limit switch to halt the motor at full height etc etc ... kinda get a feeling you should leave this well alone with your experience, the minute you make a alteration or replace a major part of the electrics you invariably become responsible the the machine/ramp you commision on completion is safe to use.
Havent even mentioned a E.stop circuit on far posts of ramp in case someone out of sight is in danger :bobby: