View the thread, titled "3 phase submain showers" which is posted in UK Electrical Forum on Electricians Forums.

Hi, I'm working in a building which has a three phase supply. There is two electric showers, sockets, water heater and lights going in a toilet block/seating area. For this I'm looking to take a 10mm 4core cable to a submain near the toilet block and running everything from here. The run is about 20m. Would this be sufficient for two showers being used in the morning and evening regularly. Should I be looking at 7.5kw to keep to loads down?

Thanks.
 
Tns 80a 3ph. From the submain i will be installing rcbos and putting each shower on a separate phase. I know 32a a phase is more than sufficient on a 10mm 4core swa feeding the sub dB then 10mm T+E to the iso/shower. Just wanted to know thoughts as showers could be used alot throughout the day. Which is why I'm opting for 7.5kw and not 10kw showers
 
Tns 80a 3ph. From the submain i will be installing rcbos and putting each shower on a separate phase. I know 32a a phase is more than sufficient on a 10mm 4core swa feeding the sub dB then 10mm T+E to the iso/shower. Just wanted to know thoughts as showers could be used alot throughout the day. Which is why I'm opting for 7.5kw and not 10kw showers
Hi do you mean your ocpd for your 10mm 4 core will be 80 amps or the supply to instalation is 80 amps
 
Just sockets and lights in the building. Sub main will have 2 showers, 3.5kw water heater, 3 x panel heaters( not sure of loads just yet on those) all plug top i do know, sockets, lights, fans etc. Its a shared office space where people cycle too hence the showers in the morning. There's also a gym near which people will come back and use the showers after or on lunch.
 
No worries. I will work out the design current. Cheers for the replys. Last question, would 7.5kw showers be better for alot of daily use over a 9.5kw one? Assuming the design of the installation was sufficient for both.
 
Just sockets and lights in the building. Sub main will have 2 showers, 3.5kw water heater, 3 x panel heaters( not sure of loads just yet on those) all plug top i do know, sockets, lights, fans etc. Its a shared office space where people cycle too hence the showers in the morning. There's also a gym near which people will come back and use the showers after or on lunch.
Your panel heaters are likely to be 2 kw or less if using something like rionte .I would possible meusure what there using just now in there existing office then work out your own loadings checking bonding conductors etc
No worries. I will work out the design current. Cheers for the replys. Last question, would 7.5kw showers be better for alot of daily use over a 9.5kw one? Assuming the design of the installation was sufficient for both.
If its just for modern office workers to hose them self down after taking the cycle lane to work I'd give them a 7.5 kw
 
I would suggest a water cylinder (possibly unvented) and an immerser.
You can get 3 phase immersers which are better for the supply, they will have a quick recovery time.

If you design it well then the cylinders will do all the showers plus the wash hand basin water as well.

This will make the load lower as you will be able to have hot water storage
 
I would suggest a water cylinder (possibly unvented) and an immerser.
You can get 3 phase immersers which are better for the supply, they will have a quick recovery time.

If you design it well then the cylinders will do all the showers plus the wash hand basin water as well.

This will make the load lower as you will be able to have hot water storage
Yes good point. I did mention this to them, but the builder and the plumber were not interested
 

Reply to the thread, titled "3 phase submain showers" which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top