you can get them upto 95mm,don't no why companies can't read cataloges .iv'e just put a 70mm 4 core in with 6.0cpc (computer say's so)computers can't read cat.either
yours benji

6.0 mm seems a bit on the lite side ,are you sure its correct:confused:
 
looked at the cleveland cable site ,yes they do 25x5 core but its got a 25 mm earth
running a seperate 16mm earth would be cheaper
 
yes 6.0mm does look small ,but comp. calc. prog.say,s its ok,it looks crap but we have elec. designers who do all the calcs. for us?


i would sooner install a 5c25mm than a 4c +16.0cpc ie only one cable to pull &only one to g&t

yours benji
 
the installation costs would be the same as you can generally get away with installing the swa and earth at the same time
that just leaves the price per metre of 25mm 5c swa versus 25mm 4c swa & 16mm earth
 
the installation costs would be the same as you can generally get away with installing the swa and earth at the same time
that just leaves the price per metre of 25mm 5c swa versus 25mm 4c swa & 16mm earth

Thats what I ment it will cost more to run a 5-core swa than 4-core and seperate 16mm cpc
 
Without knowing the full facts I see that no mention has been made of making the remote supply TT. This has the advantage of not requiring a CPC. The Swa is broken on entry to the remote building and is bonded at source. RCD protection is of course required and an earth stake.
 

Reply to 3 Phase Supply, Need A Seperate Earth in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
706
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
893

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top