Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.
 
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.

There is no seperate CPC. The SWA is earthed but i wasnt confident in using this as a main earth for the installtion of the building because of the join.

If you are concerned that there is a problem with the joint cut it out and re-joint the cable properly.
 

Reply to the thread, titled "3 phase supply to classroom, unsure to TT?" which is posted in Commercial Electrical Advice on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top