Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.
 
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.

There is no seperate CPC. The SWA is earthed but i wasnt confident in using this as a main earth for the installtion of the building because of the join.

If you are concerned that there is a problem with the joint cut it out and re-joint the cable properly.
 

Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
590
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
771
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
838
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top