Hi!
Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right?
For example: three phase 30kW appliance, 10mm 90 degree SWA, 45 meter run.
30,000/sqrt3/400 = 43.3A = Ib
from the table 4E4B, a 10mm cable gives 4.7
So then 43.3 x 4.7 x the 45 meter run gives = 9157.95 mV
gives 9.157 V
9.157/400 = 0.02289 = 2.289% voltage drop
Is that right?
Thanks!
Ben