If you are running a single phase board in a commercial premesis, its the only board in the place, but the incomer is 3-phase with a 3-phase meter but only single phase leaving the meter, would you still double the KA?
 
Guessing what is being asked is that there is a three phase supply to the building currently and only a single phase is being used to supply the lone DB for the premises, and he just wants to know if to get your PFC Ka value you still have to use the rule of doubling the reading as if it where a three phase DB using all the phases. just a guess.
 
If thats the question and its a single phase d.b. the answer is no
It will be single phase supply even though there is a three phase head installed
 

Reply to 3-phase in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
588
  • Question
Three phase or single phase it is not correct.
Replies
1
Views
550

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top