have a customer with a 3036 rewireable board. i Need to provide rcd protection for 1x30a ring circuit and 1x5a lighting circuit for additions. my plan is to remove the ring main and lighting circuit from existing fuse board.
From one of the now spare ways run a 6mm2 t+e fused at 40a to a new 2way 63a 30ma C.U. the ring main now on 32a mcb and lighting 6a mcb both circuits now rcd protected.
anyone see any issues ??
Reply to 3036 rewirable rcd protection in the UK Electrical Forum area at ElectriciansForums.net
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...